Well, when I saw this I called and had them save one for me at customer service.
<geek>
VA is Volts X Amps...which "may be watts". It would be watts in DC circuits, but in AC there is a pf. or power factor. IF this is 1 then VA=Watts.
However, if less (cap. or inductive load) then it will be less.
So, 500VA is 500watts, IF pf =1...which in this case it is NOT (500VA but 250 watts)! Some loss surely is due to powering the inverter as well.
Power companys HATE pf. <0.85 or so, and in LARGE computer centers make you add Power Factor Correctors...I have seen/measured 0.67.
WHY?
Because you pay in WATTS but they MUST provide the required AMPS...which they will not get paid for! This is also why Breakers can trip when WATT load seems OK. Oh well..."who asked me" right?
</geek>
<geek>
VA is Volts X Amps...which "may be watts". It would be watts in DC circuits, but in AC there is a pf. or power factor. IF this is 1 then VA=Watts.
However, if less (cap. or inductive load) then it will be less.
So, 500VA is 500watts, IF pf =1...which in this case it is NOT (500VA but 250 watts)! Some loss surely is due to powering the inverter as well.
Power companys HATE pf. <0.85 or so, and in LARGE computer centers make you add Power Factor Correctors...I have seen/measured 0.67.
WHY?
Because you pay in WATTS but they MUST provide the required AMPS...which they will not get paid for! This is also why Breakers can trip when WATT load seems OK. Oh well..."who asked me" right?
</geek>